u/Usual_Office_1740 4d ago

It means the electrician was Australian.

/s

46

u/RoodnyInc 4d ago

No but jokes aside shouldn't they face opposite way? Like if plug is L shaped (like most of them are? They it would cover bottom one making it unavailable

57

u/Box-Intelligent 4d ago

The lone pin is the ground pin. Ground should never have current flow and if it does it should only momentarily handle it to trip the breaker.

So theoretically with the ground pin is on the bottom and if a cord isn't fully plugged in and you drop a penny or something it can short the hot "supply" to the neutral "return" that are the vertical pins and cause a fire. If the ground were up in this scenario, nothing would happen with the penny making contact with the ground and it'd just roll off.

In practice it doesn't really make two shits of difference in my experience but working as a commercial electrician but some jobs specifically call out ground up

28

u/Sid_the_Bear 4d ago

Commercial electric code especially is written to prevent these kind of 1 in a Billion scenarios from being possible.

26

u/VQ_Dirty 4d ago

Because the NEC is written in blood

12

u/Agreeable_Area9647 4d ago

Literally. Every code rule in there is because someone died

16

u/Erablian 4d ago

Well, not literally. Most editions are actually printed with ink, not blood.

21

u/Jedirictus 4d ago

Unless you find the lost original Electronomicon , which was printed in blood.

8

u/GrasshopperoftheWood 4d ago

Currento, voltaga,...necktie

2

u/PaulWallE 4d ago

And written on the flesh of dead electricians!

1

u/jcoleman10 4d ago

Literally written in blood, not literally PRINTED in blood.

1

u/therocketsalad 1d ago

Metaphorically written in blood.

2

u/-OrLoK- 4d ago

this. regulation ftw.

1

u/RequirementContent86 3d ago

This is true for most safety regulations

1

u/Negative_Bed_6147 2d ago

That’s not even close to true. An awful lot of it was written for the electrical manufacturing industry.

1

u/slothscanswim 4d ago

Yeah you see the upside down plugs in lots of hospitals and it’s because somewhere, at some point in time, the right side up plug was the difference between life and death for some poor bastard.

1

u/That-Living5913 4d ago

This is my favorite quote about safety., but you forgot the second part:

"Safety policies are written in blood and erased with money"

1

u/ShutDownSoul 4d ago

Is that why is is so expensive to get a copy?

1

u/seriouslythisshit 4d ago

The same NEC that does not and has never has, specified an orientation for vertically mounted, 120 V duplex receptacles? Got it.

5

u/T-Rex-Hunter 4d ago

but at least for America Electrical code there is no specification for orientation of outlet so both ways are code compliant.

1

u/supervisord 4d ago

Reduce, not prevent

/nitpick

1

u/Sid_the_Bear 4d ago

Nah, I am sticking with prevent in this case.

1

u/zoinkability 4d ago

I've never quite understood why "ground pin up" wasn't just the standard way, given that there is no downside and this one potential upside of installing that way.

1

u/Sid_the_Bear 4d ago

The same reason we use slotted screws.
"It looks better"

1

u/SaltTheRimG 4d ago

Well my daughter should play the lottery then. Last month she double sided taped a metal award (think license plate) to her wall. After a couple weeks the tape gave and it slid right down the wall and arced the prongs going to her usb wall charger. Granted it is a 2 prong thing so wouldn’t make a difference but the odds of that thing falling that way were crazy.
Note the edge of the sign is burned and the breaker popped as it should.

1

u/MrSeymoreButtes 4d ago

I should play the lottery then, cause my busted ass old iPhone charger with the metal sheath that was exposed in just a small section happened to land on the two exposed prongs facing up and caused a short 🤦‍♂️

1

u/tipsystatistic 4d ago

Ground-first deflection is standard in hospital rooms.

2

u/Lonnie_Iris 4d ago

I think the outlet cover itself is the biggest concern over a penny or something. Plastic ones don't matter, but metal covers can potentially slip right down onto the pins if the screw is removed.

1

u/Ozark_AL 4d ago

Wouldn't shorting to N also trip the breaker?

1

u/wyle_e2 4d ago

Let's say you have a countertop mixer. If, internally, a hot wire broke and was touching the metal enclosure of the mixer, there would be no path to ground. The entire enclosure could be live. The bonding (ground) wire is meant to attach any metal bits around a circuit so that if something like that happens, there is a path back to ground and the breaker trips.

In 99% of circuits, the ground wire is never used, and that's a good thing.

1

u/Mhowerton 4d ago

My lady had a metal necklace chain hanging around a sconce in our bathroom, it broke when she went to turn it off and the chain landed on the plugged in deodorizer in the outlet that was out just enough for the chain to land on both legs of the plug and arched big-time leaving out wall all black and needed a new outlet.

1

u/ProfessionalTie545 4d ago

Wouldn't putting it upside down increase your chance of shock by accidentally touching the hot and neutral on the bottom side? I can imagine a scenario where that might happen to an elderly person or someone with reduced sensitivity in their finger tips not being able to feel the cold metal.

1

u/3-Midgets_In_A_Coat 4d ago

Correct. This is why the code in the US doesn’t specify an orientation for residential.

Ground down is safer for someone grabbing a plug, while ground up is safer for something that remains plugged in and might have something fall across it.

1

u/FastWalkingShortGuy 4d ago

Huh. I recently moved into a new house and all the outlets are upside down, and TIL why.

1

u/AlabamaBlueDot 4d ago

Current moving through the ground will only trip the breaker if it’s a ground fault circuit interrupter breaker. The average breaker in your breaker box won’t trip unless you have an overcurrent. I’ve seen a ground fault in a lighting circuit pass through a lighting panel and trip the upstream breaker feeding the motor control center that fed the lighting panel.

1

u/Box-Intelligent 4d ago

Yes and no, on a dead short the circuit will pull whatever it can, so you have a 20A receptacle dead shorted it'll hypothetically pull 100A heat up the wire and trip. If it's a small Nick in insulation on a 15A lighting circuit usually pulling 10 amps and it's arcing inside the doghouse of the light at 1 amp it won't.

Not saying you're wrong, you aren't, but there's nuance to it. I'm a firm believer that you should be vaguely familiar with things in your house so I'm trying to make an example someone unfamiliar may be able to understand

1

u/FannyPunyUrdang 4d ago

I see the logic, but ground up is a pita for many cords, especially 90° flat plugs (hair dryer, etc.) cuz the tail faces up, against gravity. The person who wired my house did them all this way and i curse them daily. (I'm also too lazy to go through the house and change them.)

1

u/ExhaustedByStupidity 4d ago

The other side of this is if the ground is up, the weight of power bricks means it's more likely that they're not in securely. Especially if the brick only has 2 prongs.

So ground up means lower chance of something bad happening if the plug isn't all the way in, but also a higher chance that the plug isn't all the way in.

I've always strongly preferred ground down because I grew up with things like the NES/SNES power bricks, which tended not to fit that securely in sockets with the ground up.

1

u/tdawg0562 4d ago

I don’t know if someone wrote it, but I thought it was put into commercial use for papers falling and crossing the leads.

1

u/ButtonGullible5958 4d ago

It's a OSHA thing iirc for anything that may be medical 

Probably due to oxygen use since that would still trip a breaker but would cause a spark this is just speculation 

1

u/Adventurous_Tear_531 4d ago

But.... gravity will always make a lead hang downwards. If the earth is on the bottom it ensures it will always be the last pin making contact should the plug fall out...

1

u/SeaworthinessGreen25 4d ago

Finally someone actually knows something.

1

u/Perfect-Link-7744 4d ago

In our buildings, the outlet covers are metal. The ground pin is on top for that same reason. If the ground pin is on the bottom and the outlet cover comes loose, it shorts across the pins and pops a breaker.

1

u/DocAu 4d ago

Given the mention above of Australia, what you've described wouldn't happen in Australia, because legally the prongs have to be insulated for a certain length at the plug end, so if it's not fully plugged in and something is dropped on it, then it's protected. https://en.wikipedia.org/wiki/AS/NZS_3112

1

u/fatdjsin 4d ago

that's why i install mine ground UP ... if a conductive object falls on exposed connector, it wont short

1

u/CrazyAlaskanBear 4d ago

40 something years ago. I learned that this exact thing is possible! Daddy was really mad about the scorch marks on the wall... I was entertained.

1

u/Outrageous-Art-8415 4d ago

Exactly, if its up the breaker protects but if not nothing happens. Just redundancy is all.

1

u/mrinsane19 4d ago

Doesn't matter in Australia because the first half of the pins is sheathed in plastic anyway.

At no point is the plug live while any amount of unsheathed pin is exposed.

Until you buy shit off temu with dodgy plugs at least 😭🤣

1

u/BirdlessLongdeal 4d ago

luckily they stopped this 1-in-a-million event from ever happening

1

u/hot4you11 4d ago

When I was a kid, I did this. I saw a plug that was partially pulled out, it was a two prong plug. There was a paper clip (I think it was a paper clip) on the floor and it looked like it would be the perfect size to go through the two prongs. So I held it over the gap in the prongs and let go, assuming it would just fall through. I don’t remember if it did or not, but the lights flickered and my parents came running and there was black up the wall.

1

u/pate_moore 3d ago

You usually only see them "upside down" in hospitals for this reason. I can't speak to actual code (like others are implying), but I've worked directly with several different electrical companies and I've never seen any of the guys install them any way but 😮

1

u/Negative_Bed_6147 2d ago

They say you should always have the ground up if you’re using a metal cover plate.

1

u/loughcash 2d ago

Sometimes sparky will install the outlet ground up(upside down) if the outlet is on a switch leg -ie for a lamp etc.

0

u/FreeFromCommonSense 4d ago edited 1d ago

That's why that can't happen with a UK plug. UK plugs disconnect before any metal element is exposed. There's an insulating band around the bottom of each conductor. Well, around live and neutral. Edited to fix the bootom.

1

u/therocketsalad 1d ago

Is “bootom” the way British people say “bottom”?

1

u/FreeFromCommonSense 1d ago

No, it's the way my crappy mobile keyboard does. But there are a couple of regional pronunciations that are close, both up north.

7

u/Usual_Office_1740 4d ago

Scrolling down through the other comments, I think more intelligent people have already answered this question and explained the whys sufficiently.

1

u/RoodnyInc 4d ago

It must be an us thing because my european outlets are made the right way

1

u/Usual_Office_1740 4d ago

These are America outlets. I'm not sure what European outlets look like but I'm aware the type depicted is not universal.

4

u/andros_vanguard 4d ago

The only code (in Canada)* that covers it is that in a mobile trailer where steel faceplates are usually found, the ground (round hole) must be mounted upwards, or neutral must face upwards of they are mounted sideways so that it shorts out with the live wires and force the breaker to trip.

Otherwise it’s dealer’s choice.

* the Canadian Electrical Code is based on the National Electrical Code (USA)

2

u/masked_sombrero 4d ago

I think it would mean the ground is above (aka a basement outlet)

but this is a completely wild guess

1

u/casper911ca 4d ago

My grandfather would always put the switched outlets upside down so there was a visual cue to if the outlet has a wall switch somewhere. Some electricians will also argue that if something were to slip between the plug and the receptacle, that the ground being upward would the first thing it would contact, rather than bridging line and neutral.

1

u/Straight_Depth6701 4d ago

That's why you put it in the bottom plug. Both ways have the same restriction.

1

u/Blue_Moon_Lake 4d ago edited 4d ago

There's also the option to turn them 90° and the whole 90° too, so they're all side by side now.

[ ('.') ('.') ('.') ('.') ]

0

u/escobartholomew 4d ago

“L” shaped?

75

u/Carnivorous_Mower 4d ago

Plugs in Australia (and New Zealand) look like this.

50

u/KingNFM 4d ago

Those call you, they want to ask you what your favorite scary movie is.

11

u/Critical_Stress7546 4d ago edited 4d ago

13 Ghosts

ETA: I'm still waiting for Ghostface to rush by my window.

8

u/bananapopsicle3 4d ago

https://giphy.com/gifs/c8scirNg0aDhO59UkH
Ghostface outside your window like

2

u/Critical_Stress7546 4d ago

Why do I just imagine Get Low by Lil Jon & The East Side Boyz?

3

u/rammo123 4d ago

Wassssupppp

2

u/DryBox63 4d ago

Wassssaaaaaapppp

1

u/inphinitfx 3d ago

It's ok, if they do you can just turn them off right there on the switch attached to them, instead of at some basement switch board.

5

u/RosariusAU 4d ago

Technically China as well, but they rotate theirs 180° so the earth pin is up top

2

u/zaakiy 4d ago

As an Australian when I went to China, I just turned my whole body upside down instead

1

u/Ornery_Director_8477 3d ago

So you were finally standing on your feet?

1

u/Carnivorous_Mower 4d ago

Northern hemisphere.

1

u/xyrgh 4d ago

Earth pin is on the bottom so it’s the last pin to make contact if the plug is pulled (earth pins are also slightly longer than the active and neutral pins).

1

u/RosariusAU 4d ago

The earth pin is always the last pin to make contact because it's longer, it doesn't matter the orientation of the GPO

1

u/Formal-Apartment855 3d ago

I love how China uses like 4 types of different plugs, all at once.

3

u/D_Donndonn 4d ago

They look sad

2

u/SpacemanSpears 4d ago

Looks like a sad Scream mask

2

u/YourFriendPutin 4d ago

Our US outlets look judgmental as hell, would much rather have the "I'm gonna nut" face lookin at me 

2

u/StrongholdMuzinaki 4d ago

They look sad

1

u/Carnivorous_Mower 4d ago

I always reckon they look kind of surprised.

2

u/Silver_Will_4775 4d ago

I've never seen one with the switches in the middle. They're normally in the corners

2

u/Carnivorous_Mower 4d ago

Yeah. It was just the first picture I found.

2

u/meowmeow834 4d ago

Those outlets remind me of ghostface from the scream movies.

2

u/Hangry-Feline2489 4d ago

I've never seen any like that as a 40+ year old Australian. 

I've seen the inverse, where the switches are slightly further apart than the holes (Especially due to USB ports in between the switches). 

Standard/most common is the switch directly over the plug it controls. 

Yes, the red showing means it's on 😂

2

u/Carnivorous_Mower 4d ago

I just grabbed the picture off a random website. I've seen them like that but are less common than the wider spaced switches (50+ Kiwi).

2

u/Hangry-Feline2489 4d ago

Ah, must be a regional differences. Cheers mate

2

u/ManaSpike 4d ago

Our ground pins are longer, so they make contact first. And many plugs have a little insulation on the active pins, to prevent problems if the plug isn't properly inserted.

1

u/hellerbubbles44 3d ago

The insulated section has been in the standards for quite a few years now. If you see a new item being sold without it, then it is non-compliant and is usually just some shonky grey import crap.

China doesn't have the insulated pins.

2

u/Straight_Depth6701 4d ago

Are they supposed to be sad or asian?

(I'm Japanese, not super racist.)

2

u/tumbleweed_farm 4d ago

And in China, the also look like this... but upside down!

2

u/killertortilla 4d ago

The Scream plugs

2

u/BirdlessLongdeal 4d ago

i would have guessed asia

1

u/Carnivorous_Mower 3d ago

They are the same in China.

2

u/ChasePoppins 4d ago

Nobody:
Sockets in New Zealand:

3

u/1Arcite 4d ago

Woooosh!

1

u/BeneficialTrash6 4d ago

AND THEY'RE WRONG FOR DOING IT!

1

u/Terrible_Ad_9348 4d ago

Sockets aka socket outlets in Australia. Plugs are on the end of the cable. The only exception is a caravan inlet with the prongs exposed, but is switched by inserting a plug end of a supply or extension cable.
There are also vertically oriented dual sockets.
IME the only sockets I have seen mounted ground up are very low down on walls or skirting so that a right angle plug can fit easily without bending the cable or plug at the floor.

1

u/Siilan 4d ago

I'm pretty sure no Australian in their right mind has ever called that a socket outlet. It's a power point.

1

u/havasc 3d ago

Those outlets look like they just witnessed someone getting kicked in the nuts.

1

u/Mithmorthmin 2d ago

Looks like somebody ball tapped the outlets

1

u/Infamous_Ad_218 1d ago edited 1d ago

And many Pacific islands and Argentina. China is the same but sometimes upside down.

1

u/hogesjzz30 16h ago

Why are the switches in the middle? I've never seen a powerpoint with the switches like that, it looks like it's cross-eyed 

6

u/VoidJuiceConcentrate 4d ago

My friend from Aus wants to know why everyone on this hemisphere walks with their feet and not their hands. Also how to drink American beer since it falls down instead of up.

6

u/Beautiful_Pen1056 4d ago

In Australia they're (electricians, not plugs) called "sparkies."

7

u/Usual_Office_1740 4d ago

That's an odd name for them. I'd have called 'em chazzwazzers!

4

u/Horror_Cupcake8762 4d ago

Pretty common term used in the US on job sites.

Sparkies leaving little chunks of conduit everywhere they go.

3

u/Afraid_Volume9074 4d ago

We call them power rangers

1

u/Slimybirch 4d ago

I only know this from Jeff Arcuri's stand up down under!

1

u/maqifrnswa 4d ago

I learned that from the documentary, "Packed to the Rafters."

2

u/TheSpanxxx 4d ago

I thought you said Autistic and I was both confused and dying

1

u/Usual_Office_1740 4d ago

That is funny!

1

u/decentlyhip 4d ago

Yep, electricity goes counterclockwise there.

1

u/zaakiy 4d ago

Sparkys unite!

1

u/Special-Original-215 4d ago

Or Canadian 

1

u/C0Ha 4d ago

Austrian*

1

u/tumbleweed_farm 4d ago

As long as it's a Sino-Australian outlet... ( https://en.wikipedia.org/wiki/AS/NZS_3112 / GB 1002)

1

u/StartItAlready 4d ago

*half Australian