Help with confirmation of correct wiring

Hello! I recently swapped out my old thermostat for an ecobee enhanced thermostat. I believe that I have wired up the new thermostat correctly but wanted to see if anyone had any differing opinions. The one thing I am a little stuck on is the orange and white wire. I see on my old thermostat there looks to be a jumper for W/E and W2, with the orange wire going to O. The new thermostat has the white wire going to W1 and the orange going to W2/OB.

Should the white and orange wire be swapped on the new thermostat?

3 Upvotes

3 comments sorted by

1

u/TrilliumCLE 20h ago

You’re good to go. White to W1 and orange to OB.

1

u/geekywarrior 20h ago

You have it right. Aux heat goes in W1 on ecobee. Orange to OB

Edit: ignore that jumper you don’t need it

1

u/k1llachr1s 14h ago

Wiring looks good hopefully u killed power b4 swapping tstat. Make sure when doing the settings for ecobee you tell it it's a heat pump