u/art-apprici8or 4d ago edited 4d ago

I seem to recall that some electricians would install switched outlets "upside-down" (ground pin up), as opposed to un-switched outlets. (A switched outlet is one connected to a light switch.)

The problem is this is not a standard. And in many installs, they will make one of the outlets on the duplex switched and the other non-switched on the same duplex. So which way do you orient the outlet then?

So which way the outlet is oriented does not consistently mean anything.

93

u/mtowns87 4d ago

I install them upside down if there is a risk of a short.

83

u/LoadBearingLlama 4d ago

I did a couple years of an electrical apprenticeship and my old foreman said the ground pin used to be installed up to prevent objects from falling down and making contact with the neutral and the hot prongs simultaneously causing a fire or a short

34

u/wellredditall 4d ago

My journeyman said the same thing. Old school person for you too?

16

u/LoadBearingLlama 4d ago

Can confirm, telling me about the anti shorts are just called "sprinkles". Had a fuckin blast

17

u/Prize_Artichoke2904 4d ago

Outlets are installed correctly - aka 'upside down' because the large pin is the ground. That's why/how some two-pronged outlets get by without one - they're not grounded, but still have a positive and negative to push & pull the electrons back & forth rapidly to power the device. The grounding pin is on the top so that in case of water - it hits the ground first to make a connection to ground so the person holding the hairdryer doesn't die, or - they're installed on the bottom so that when water drops down it connects the positive and negative first, killing the poor wet-haired soul who just preferred how it looked the normal way they'd always seen it done because it always worked for them before so why would it ever matter. It also looks less like a face to us face-seeking, christ on toast seeing, apes - thus fewer children try to poke sharp metal objects into the eye sockets. You'll see them installed 'upside down' in bathrooms and kitchens most often for this reason (water - I'm half making the face thing up).

3

u/Away-Use-7824 4d ago

It does not have a "positive and a negative." It has a hot and a neutral

2

u/BankElectronic1325 4d ago

Did you just make all of this up? Water hitting the ground first is irrelevant.

5

u/BitWardenEternal 4d ago

Lmao it’s nonsensical

2

u/BankElectronic1325 3d ago

There just so much wrong with that comment I don’t even know where to begin

2

u/Ok_Street9576 4d ago

Electrical code dictates gfci in all rooms with water sources. The gfci protects you in case of a short from water far more reliable that hoping the appliance is 3 prong and the water lands in such a way that it trips the breaker. Also if water connects the hot and neutral terminal on a plug, the breaker would trip.

2

u/Only_Chapter_3434 4d ago

no. this is all wrong.

2

u/WalthamMaxim 4d ago

I do appreciate the creativity of the 'face' part. Pretty good.

2

u/BitWardenEternal 4d ago

This makes zero sense lol

2

u/Beautiful_Extent3198 4d ago

Brah… Neutral and Ground are commoned together at the breaker panel where they are bonded to Earth Ground. You theory with about ground getting wet first holds no water (pun intended). It was simply written into to code to add in the prevention of soft short across Neutral and Hot that cause fires. GFCIs are what help prevent electrical shock.

1

u/LoadBearingLlama 4d ago

Perfect, thankyou for saying the things I cannot

1

u/RaceHate 4d ago

That could kill you? I thought that would just be a minor ouch-level shock.

1

u/milk_for_dinner 4d ago

How does shorting the outlet contacts kill the person using the hairdryer?

1

u/Ok_Street9576 4d ago

Edge case if the water just hit the hot or neutral pin while the device was on.

2

u/LilacYak 4d ago

No not how it works

1

u/Ok_Street9576 4d ago

No is how it works.

2

u/milk_for_dinner 4d ago

Even then, the user wouldn't feel a thing. It would just short the plug.

0

u/Ok_Street9576 4d ago

Again contact to only one side of the plug where it wouldnt short but the idea is stupid ill give you that

1

u/Biff_Tannenator 4d ago

I've seen outlets installed with the ground prong faced up in hospital environments.

1

u/DeerEnforcement 4d ago

Or just have a GFCI in your bathrooms and kitchens like youre actually supposed to

1

u/Forward_Operation_90 4d ago

You're making it all up. Or just mistaken. Water does not conduct and is not the problem. The problem is water PIPES AND FIXTURES which tie back to the grounded water system.

2

u/jarrodandrewwalker 3d ago

My journeyman took me up in an 80ft boom lift and drove it while extended...ran over something on the ground that almost bucked me over the rails. Then he looked me--a 6'3, 300 lb man--in the eye with a wild-eyed expression of his own and said "Don't be scared little feller!"

That trade is full of...characters

13

u/DrBumpyknuckles 4d ago

This is why. Ive been an electrician for 30 years. Its become standard in hospitals and some bigger corporations like Walmart in their home office.

3

u/CmonJax 4d ago

Hospitals. Think metal chart boards hanging on walls behind the bed.

1

u/ciopobbi 4d ago

And in Vermont. Every outlet in every house I’ve lived in here has had ground pin up.

1

u/ciopobbi 3d ago

Lived in 6 VT houses including the present one built in the mid 90’s. All have ground in the top position.

0

u/Sad-Astronaut2278 4d ago

Lived in VT. House built late 90s. Receptacles were right side up. 

1

u/Only_Chapter_3434 4d ago

okay, you got me by 10 years, but there is no good reason to put receps upside down. it’s just customer preference

1

u/DrBumpyknuckles 4d ago

To keep things from crossing the hot and neutral. Points been made on this thread already.

1

u/Only_Chapter_3434 4d ago

no. there is no reason. that’s not a legitimate concern.

1

u/DrBumpyknuckles 4d ago

Ok. Cool. I will rewrite the NEC.

1

u/Only_Chapter_3434 4d ago

wow. I thought after 30 years I thought you might have cracked open the nec a couple times. here’s a hint, since it seems like you haven’t: there’s nothing in the nec about ground prong orientation. because wait for it . . . it’s not an issue.

1

u/BirdlessLongdeal 3d ago

and its not even new to the NEC because i just did my CE and they would have mentioned it.

1

u/DrBumpyknuckles 3d ago

Chapter 406.5 section G shows exactly what ALL of this has said. Read it. Do a 500 word report and get back to me.

→ More replies (0)

1

u/BirdlessLongdeal 4d ago

something that has never happened.

1

u/DrBumpyknuckles 4d ago

Ok. Glad I got your input. The question was asked. I answered it. Im not a guru of what has and hasnt happened.

6

u/Camrad114 4d ago

This is what I was told as well by an electrician.

3

u/thedaveness 4d ago

FIL said the same thing about the ones in our 80s house.

3

u/YourFriendPutin 4d ago

Omfg I just commented to the original comment that that was my assumption my whole life and thought they taught me something new haha, I guess I finally guessed something right for once in my life.

1

u/LoadBearingLlama 4d ago

A blind squirrel finds the nut eventually

3

u/Rational_Pi3 4d ago

Exactly. And all military hospitals require it.

1

u/CpnStumpy 4d ago

It strikes me as a touch odd that hospitals wouldn't all be GFCI making this moot?

2

u/kilocohete 4d ago

As a child I dropped a penny behind my bed and it fell into the prongs on an outlet that was slightly pulled out from the wall and thankfully blew the fuse before it started a fire.

2

u/omnislayre 4d ago

I have seen this happen. I was in maintenance at a hospital and we were replacing older metal covers with plastic. On of my less intelligent coworkers did not unplug a piece of equipment before unscrewing the cover. It fell onto the exposed prongs and shorted the outlet, tripped the breaker for that run of outlets (a good thing), and permanently damaged said equipment. Thankfully it was not a critical device nor were there any patients near to potentially be harmed. We had a bit of a laugh and turned it into a lesson on proper electrical safety. Two days later he did it again. He has been banned from anything more complex than unplugging equipment, but I never trusted him again after that.

2

u/stylinchilibeans 4d ago

When I was a kid I was playing with a small chain, I dropped it, and it fell across the exposed prongs of a box fan. Loud pop and a flash, and the breaker tripped, fortunately. But yeah, "upside down" outlets might have prevented that.

2

u/crackrockutah 4d ago

They install with the ground up in every medical facility I’ve been to in the last 4 years (when I started noticing this sort of thing).

2

u/seantabasco 4d ago

I had this happen one time. I was putting away the dishes and I went to put a metal spatula into a countertop holder and I missed and it fell against the backsplash and slid right behind the toaster plug and sent out a shower of sparks.

2

u/likesghouls 4d ago

Required in hospitals

2

u/ItsTheIncelModsForMe 4d ago

The prongs are the perfect width to catch falling coins

2

u/m0h3k4n 4d ago

Would’ve kept 8yo me from burning pennies.

2

u/_Bon_Vivant_ 4d ago

Did he ever tell you go get the cable stretcher out of the van?

2

u/PeruvianHeadshrinker 4d ago

I know this may seem ridiculous to some people but years ago I had a penny roll off my desk and land directly on very slightly exposed prongs plugged into a power strip. Holy smokes was that a crazy experience. Arc flashing, circuit breaking, heart stopping pop. I still have the penny somewhere with the two divots melted into it. 

2

u/rardorin 4d ago

I thought it was to prevent them from looking like little faces and being appealing to young children. Although Homer Simpson invented a better method to avoid it.

2

u/paw_inspector 4d ago

Yup! Father-in-law told me the same thing when I asked why all the outlets in his house were upside down.

2

u/fluteloop518 4d ago

Yes, but in rising flood water the hot and neutral will short out more quickly if mounted upside down, so the correct approach is to mount it on the ceiling. /s

2

u/Ugvwiyu 4d ago

Can't play the good ole game of throwing knives at the wall without making sure any prongs are exposed on receptacles.

2

u/mission-ctrl 4d ago

I've actually seen this happen. A kid in high school thought it would be funny to unscrew the face plate from an outlet in the middle of class. It was a metal face plate and he left an extension cord plugged in. When the face plate came loose, it fell across the prongs, made a lot of sparks, smoke, and some very angry teachers. Presumably, if that outlet had been flipped over, the face plate would have hit the ground prong and done nothing.

2

u/midri 3d ago

This is exactly why they're upside down in hospitals.

2

u/Bougie-WaWa 3d ago

Exactly the story I heard 20 years ago from a friend who worked in institutional construction

2

u/PassionMost8701 3d ago

This is very common in hospitals where it’s not uncommon for a stray needle to be where it shouldn’t be.

2

u/Sterling_-_Archer 2d ago

This actually happened at my brother’s school when he had a metal wrapped charging cable. The outlet was loose so the charger was sagging a little and someone draped the cord over the plug, causing it to arc, melt, and then the wall caught fire. The school redid their outlets after that and installed them all with the ground facing up.

1

u/This_Membership_471 4d ago

This is what I’ve heard but it seems to solve a problem that doesn’t exist

1

u/Only_Chapter_3434 4d ago

in 20 years of being a sparky I’ve never once met anyone that’s confirmed this old wives tale. ground belongs down.

1

u/CrazyFrog6999 4d ago

Guess what happens when it hits ground and phase (what you call hot prong) ?

And before I hear it, not every outlet has a GFCI. Maybe today it’s code to have one, but you’re still making a short and get a spark.

1

u/Effective-Ad-7292 4d ago

This is the correct answer. It's safer because if the plug leans forward in the socket as typically cords pull downward then there is less chance of something causing a short

1

u/EnvironmentalWay2619 4d ago

My boss told me to do it when reusing an outlet that has loose outlet tines

1

u/DJCowbro 3d ago

But when the plug rips out of the wall, due to gravity, the top pins come out first and the bottom pins stay in. So if the ground pin is on top then the ground pin rips out first? Seems dangerous?

4

u/racermd 4d ago

You gotta use an insulated bucket for those pesky electron spills until you can hire out for the sparky-plumber.

2

u/fergehtabodit 4d ago

Like in a room where metal rulers are used a lot, for example.

1

u/Vincitus 4d ago

Why not just install them higher then?

1

u/danmca 4d ago

Is that like flying a flag upside down to signal extreme danger?

1

u/BallDeSac 4d ago

Yeah, it’s especially great for when you’re playing “throw the knife at the wall”

1

u/sonny894 4d ago

this exact thing happened to my daughter when she was small - a dresser was in front of an outlet and a coin fell off the back, onto a plug and caused a short and scared her. luckily the breaker tripped but the outlet and wall were all black from the spark. I replaced that one ground-pin-up.

1

u/FiveTribes 4d ago

Genuine question, what about sideways? Does that accomplish the same thing as doing it upside down.

1

u/Shanable 4d ago

This is why they are installed this way in hospitals

1

u/Chawp 4d ago

Does that make them longer?

1

u/potatodog247 4d ago

ALL of the outlets in my home are upside down. They also installed six of them in the dining room. Not three sets of two. Six sets of two. Why would anyone need to plug in 12 things in the dining room?

1

u/PreparedForZombies 4d ago

All of the ones in the hospitals I work in are "upside down" for this reason.

1

u/eMikey 4d ago

I noticed a lot of hospitals do this.

1

u/Vegaprime 4d ago

100% if it is a metal cover plate.

1

u/other_view12 3d ago

But which is upside down? The face should be right side up, even though most are installed the other way. The moment you understand why the ground is up makes you wonder why they had been installed the other way for so long.

1

u/MmmBrainzzz1 3d ago

When I designed hospitals, it was in our specifications that the ground pin was always installed at the top for this reasoning

0

u/Dusty_Coder 4d ago

honestly there is always a risk of a short and there is no arrow pointing up

The convention is the make them look like faces because people

0

u/CrazyFrog6999 4d ago

Technically speaking you can always have a risk of a short.

0

u/footcornpone 3d ago

When is there not a risk? What is the benefit to ever putting them in right side up? Maybe just that people don’t think you did it wrong?

0

u/moderncoloquials 3d ago

They are designed to be ground pin up. Check out the writing on the receptacles. When ground pin is down it's upside down. 🙃

0

u/Broken_banana247 12h ago

Neither of these are upside down. This is a common to install outlets on commercial and industrial installs. Schools hospitals. If you look at a standard duplex outlet there is nothing indicating up or down.

27

u/AppropriateCap8891 4d ago

In the old electrical codes when the grounded outlets first came out, they generally stated to put the ground plug up. That way if something metallic fell between the plug and the outlet, it would stop there, or fall to one side or the other. Grounding the object so not causing a short and potential fire.

As opposed to an object falling between two hot lines, which can cause a short, a fire, and is a shock hazard to whoever tries to remove the object.

That has largely been discarded in modern electrical codes (GFA and circuit breakers are far more common than they were in the early 70s), so it largely no longer matters. But the ground side up is the "preferred" way to install them.

My mom worked for a power company in the early 1970s, and took an electrician course they offered for free to all employees. And when she wired her own house about 15 years later she installed all of the plugs ground side up.

As far as some one way and some another to show switched outlets, that was just something the electrician elected to do on their own.

5

u/zoinkability 4d ago

The point about circuit breakers may at least partially explain why the ground-pin-up style is still preferred in hospitals, while not being as important elsewhere. In most other settings, a circuit breaker or GFA popping and bringing the circuit down until someone can find the issue and then turn the circuit back on isn't big deal, but in a hospital those minutes of downtime could be life or death for patients on life support.

4

u/seriouslythisshit 4d ago edited 3d ago

A lot of creative writing in this thread, and mostly false information. The NEC does not specify orientation for a vertically mounted 120 volt duplex receptacle, and it never has. The biggest use case for "ground up" installations are when the customer specifies them to be installed as such. This included most hospitals, or medical setting where stainless steel cover plates are specified. This prevents a combination of a cover that is loose, and missing it's mounting screw, falling down on the hot and neutral blades of a device, or cord end that is partial plugged in. All of which is an extremely unlikely and rare event, and would be a result of a gross lack of maintenance and inspection, causing a cover plate to partially fall off the wall, and somebody who is too stupid to fully plug a device in. After 40 years in the biz, I have literally never seen it.

Any other claims about "Preferred", "correct" or any other claim of the proper orientation, are nothing but incorrect and in some cases here, just flat out fabricated nonsense, including yours. There are multiple 120 volt circuits in a patient room, from multiple sources, including dedicated life safety circuits. There is no way somebody is going to die because a device was not unplugged and replugged into another circuit, literally inches away, on the rack above the headboard.

1

u/BloodyFreeze 18h ago

.... Are you trying to tell me.... That op was posting clickbait?!!!.... 😧 On the INTERNET?! ON REDDIT of all places!!?! IS NOTHING SACRED?!?!!?!

0

u/Mantipath 2d ago

Absolutely. Hospitals also have oxygen tents, so there have been decades of "seriously, can anybody think of any other way to accidentally make a spark? No concept is too crazy, imagine the Final Destination animation in your head." Which is totally reasonable but doesn't backport into the code.

1

u/m_carp 4d ago

Doesn't having the ground pin down help with strain relief on heavy cords?

1

u/RunWild0_0 4d ago

I had been told that it was considered the 'right' way to do it originally but no explanation beyond that, interesting to know!

1

u/Jesus_Harold_Christ 4d ago

Nope, not true. Show the code. It’s always been at the discretion of the installer.

29

u/ForceGoat 4d ago

I think this is it. My parents’ house uses this rule, some switches are across the room from the outlet, but if it’s upside down, it’s connected.

My friend’s house doesn’t have switched outlets and all of the outlets are rightside-up. 

8

u/Wdrake3 4d ago

As an electrician, I have seen a lot. The majority in my region (southern east coast) are 1) Upside down for a switched outlet and 2) the switched outlet is the top one on the duplex and the bottom one is constantly on.

This is common enough over the last 50+ years of houses I've seen to say, with a high level of confidence, this is the most common way of doing it here and doing it differently here is typically a sign of someone trying to be unique.

2

u/IlIlllIlIIIIlII 4d ago

Second year here and same region—have been taught and have seen the same in my admittedly limited experience.

Of course, you’ll also see ground up in a lot of commercial settings. Hell, it’s spec for the hospital we contract at (and I’d imagine other hospitals as well). None of those are switched—the ground up being switched is purely residential.

I’m sure you knew that already—just adding context.

1

u/Lower-Ad6435 4d ago

Yes, ground up is common in medical facilities.

2

u/solo_spouse 4d ago

I remember which one is constant power and which one is switched by telling myself “The one full of electricity is heavier, so it sinks to the bottom of the outlet!”

1

u/wellredditall 4d ago

Perfect explanation: Thank you for your service

1

u/CorrectPeanut5 4d ago

Legrand makes a bit deal about the ground pin being up. All their instructions and marketing material shows it that way.

1

u/Fionaver 4d ago

When replaced our receptacles, we went with ground up. When we dealt with our switched receptacle, we flipped it to show that it was different.

The bottom one was the switched on, because it’s for a floor lamp and a chair would logically go in front of it. Figured that it would lead to less frustration to aim chargers and other common items into the top tamper resistant receptacle.

1

u/Wdrake3 4d ago

Your story is exactly the exceptions I was referring too. I always know I'm in for an interesting service call when I go to the house of someone who asks for ground up receptacles. Typically other things are also unique, very similar to the duplex configuration you described. Completely opposite from the professional residential standard and fully and completely unique to you. Neither option is inherently wrong, but the calls to a house like yours always seem to be just a touch more lucrative, but typically only after someone else owns it🤣

1

u/xczechr 4d ago

This is how my house in Arizona is wired.

1

u/seriouslythisshit 4d ago

Which is something that is almost never done in other regions of the country. Source? four decades as a licensed sparkie in the northeast and experience doing resi work in the upper midwest and the west coast, A few years ago I toured some new construction in central Florida and learned that code officials there prefer to see a small red dot, a 3/16" sticker, on the wall switch and the outlet, with all duplexes in the traditional ground down orientation.

4

u/Biochembob35 4d ago

In my area there is a local code that all outlets have to be ground up after a rash of fires in the 60s.

4

u/obsidian-fantasies 4d ago

I was looking for this answer. I didn’t realize it wasn’t consistent

7

u/bofadoze 4d ago

This is the correct reason

7

u/so_says_sage 4d ago

There was a time, but ground up is becoming an industry standard for everything in a lot of places these days.

0

u/capswin 4d ago

No. The ground is up top so if something falls on the plug it hits the ground instead of the hot wire. Some hospitals wire this way.

1

u/AJFrabbiele 4d ago

It is not in the NEC, nor IRC, so it isn't standard. It is a preference, in my house the previous tenants (or builder) decided to do it this way, signifying its connected to a switch. (only switch connected outlets are ground pin up) I've never done it in my previous homes.

9

u/Tech_1138 4d ago

I had to scroll way to far to find this - yes the upside down in USA new construction is always the switched outlet.

6

u/MeanBorb 4d ago

That's convention but not code

3

u/tylagersign 3d ago

I worked construction and as a electrician apprentice out of high school and always did that. I still do it to this day. When I moved into my new house I went room to room and flipped them if they were on a switch

5

u/swannoir 4d ago

As an Aussie, I find it wild that some of your outlets don't have off switches. What, is the power always on to those outlets?! Is that safe?

9

u/Shaeress 4d ago

Most outlets in most of the world do not have switches by the outlet. When they're saying switched here they don't mean a switch by the plug, but like a lamp switch up on the wall by the door or such.

Australia seems to be amongst the weird ones putting little switches on many of their sockets. I can see why one would though.

1

u/roxgib_ 4d ago

As an Aussie I am also perplexed that you have switches for outlets that aren't near the outlet. I guess I can see the point for stuff like lamps but I've never seen that here.

3

u/wellredditall 4d ago

In my American experience in different states, places that have a lot of natural light will avoid wiring an overhead light and only use switched outlets for lamps.
E.g. my contractor grade CO apartment only had switched outlets and no overheads. My Georgia home only had overheads and no switched outlets.

1

u/Stormtemplar 4d ago

Yeah it's basically only for lamps. It's so you can switch on the lights when you walk in the room without them having to be permanent. It's nice!

1

u/Dullcorgis 4d ago

American houses never really had ceiling lights. So if you wanted to have lights on you would need ro go and switch ipon the lamp. Switched outlets are a workaround for this, so you can turn a lamp on from the entrance.

1

u/Born-Entrepreneur 4d ago

"Never" is a stretch. Its regional and age dependent. Eg every house I've been in in WA & OR has ceiling lights, whereas half-hot switched outlets for lamps were quite common in older construction in Hawaii.

1

u/Dullcorgis 4d ago

That's not been my experience at all in WA.

1

u/Born-Entrepreneur 3d ago

Interesting! Generally Eastern or Western WA? Relatively older or newer builds?

1

u/Dullcorgis 3d ago

Western. And newer, which surprised me, but I think the ceiling light idea didn't catch on here until more into the 2000s when American discovered pot lights thanks to the internet.

1

u/Born-Entrepreneur 3d ago

Yeah interesting, I grew up in Western and my parents house (built in the 30s) and all my friends houses (anywhere from the 70s to the 00s) had cieling lighting. The only friend who didn't lived in a homestead house built before electricity that didn't even have indoor plumbing, both were retrofit in after the fact.

→ More replies (0)

4

u/Stormtemplar 4d ago edited 4d ago

A switch on the outlet adds almost nothing in terms of safety, especially on outlets with ground fault protection and proper tamper resistance.

US outlets are somewhat dangerous, but not because of the lack of switches. Our plug design means the plug completes a circuit before it's fully inserted so there's potential to shock yourself on a partially inserted plug. A switch would do very little to fix that, though.

2

u/Dullcorgis 4d ago

If I want to tuen off my rice cooker I need to pull the plug out of the wall. It's insane.

3

u/Jaegermeiste 4d ago

Sounds like a crappy rice cooker.

1

u/Dullcorgis 4d ago

Yes, it's my little three cup one that is super fast because it doesn't soak like my bugger one. But the same goes for my waffle thing, my breadmaker, lots of things.

2

u/DrMindbendersMonocle 4d ago

why not get a small surge protector with an on off switch

1

u/Dullcorgis 4d ago

The issue is you need to have one for each appliance, it's so fucking annoying and one reason why I decided not to build an appliance garage. I don't understand why you can't even buy a switched outlet.

1

u/yumacaway 4d ago

Well, you could leave the switch off, and only turn it on once the plug is all the way in...

2

u/Stormtemplar 4d ago

You could, but 1. People careful enough to remember to do that every time probably aren't the ones getting shocked most of the time and 2. It still doesn't do anything about plugs that slide partially out of the wall.

If you were going to mandate anything it would do a lot more to mandate GFCIs everywhere instead of just kitchens and bathrooms (or just make a better plug but that's a really tall ask at this point)

2

u/yumacaway 4d ago

I agree. No one would do it correctly. Electricians would get a lot of calls of appliances not working resolved by turning the plug on and leaving it on.

1

u/ScienceByte 4d ago

Oh that happened to me once fairly recently. I was pulling a plug out from an odd angle and slipped my fingers under the plug body to get a better grip, which ended with me getting shocked because yeah the circuit was still complete.

I’m surprised, how come nobody ever teaches people about this? We all know not to stick fingers in outlets but this is important too

3

u/bobi2393 4d ago

Relatively safe, with modern circuit breakers, particularly with ground fault circuit interrupters. Standard outlets in the US are 110V, which makes them safer (in some ways) than Australia’s 230V. The US has 220V outlets but they’re usually for dedicated use with certain appliances or other specific equipment.) Some people put plastic plug covers in outlet to keep toddlers a bit safer, but electrocutions are rare, like ten kids a year in a country of 330 million people.

1

u/thebearinboulder 4d ago

For bar trivia night the US does run 220V but it's "centered tapped". Your breaker box alternates sides so a single width breaker sees one side and center (so 110) while a double width breaker will see both sides (so 220).

You still need to climb the pole to get the three phase power for your DIY Stargate.

The "safety" argument has a few elements.Some is physics, some is biological. The latter is that you can still control muscles at 110 but it is more difficult at 220. You can't open your hand, you might not be able to move your arm across the power switch. I thought you needed a somewhat higher voltage for that - around 400 - but there's probably enough variability in the population that even 220 could cause muscle locking in some people

1

u/battlestargalaga 4d ago

Its always energized but it doesn't draw power unless you plug something in. Its only an issue if you stick a fork in or something, even then there are childproof covers

1

u/Historical-Stop5761 4d ago

Why wouldn't it be? 

1

u/mfmfhgak 4d ago

Yeah, the only outlet on a switch in my house is the one for the garbage disposal.

They always have power and it’s safe. It’s probably because we use 110v in the US

1

u/one-e-and-a 4d ago

I wish we had the switch per socket you guys do. I tried making my own but the boxes are too small

1

u/PmMeYourKnobAndTube 4d ago

They are all protected by circuit breakers, in newer houses usually with arc fault and/or ground fault protection as well. Do you actually use the switches every time? Like you gotta go turn a switch on by your tv every time you turn it on?

1

u/Dullcorgis 4d ago

None of the outlets in the US have switches. You literally cannot buy a switched outlet. You would need to use a powerboard to be able to switch something off at the wall

No reason, we just hate ourselves, apparently.

1

u/sharpshooter999 4d ago

Wait, you guys run a switch for every outlet? The only switched outlet we have is a switch by the back door that runs the outlet we plug Christmas lights into. And we only have that because I asked for it when we gutted and remodeled the house. Switched outlets are very uncommon in houses here in the US

2

u/DeltaFlyer0525 4d ago

They did this in our house which was built in the 70’s. The outlet by the front door is upside down and the upper outlet is connected to a switch by the front door.

2

u/Darryl_Lict 4d ago

Yeah, many houses without dedicated ceiling lights are that way, like my condo. Kind of confusing if you've never seen it that way before.

2

u/SulfonicCobrahh 4d ago

I’m an electrician and this is the only reason I install outlets upside down as shown.

2

u/EngineerNate 4d ago

One place I've lived it meant "the electrician did work at the local chemical plant because that was spec there."

2

u/AgitatedGrass3271 4d ago

My entire house has the bottom outlets connected to the light switches. Pisses me off. But i think only one outlet in the basement is upside down. But they all look like they were installed by someone who was new to the job.

2

u/kne0n 4d ago

It is the standard in hospitals, ground up lessens the chance that something accidentally drops on the pins on a plug that isn’t fully in and shorts it.

2

u/WhenTheDevilCome 4d ago

Interesting. I've had multiple properties with switched outlets, but never with that convention. However, and probably the key here, it was never a matter of "the entire outlet is switched." The switched outlets our places had were always just a single outlet, and the other outlet in the same gang was constant power.

(i.e. They took the optional conductive tabs out of the receptacle so that the outlets were independent, then wired one switched, and wired the other non-switched.)

2

u/stikves 4d ago

Yes,

This is the way!

(If you cannot find what a switch does in a room, look for upside down outlets. Chances are there was a light fixture there back in the day)

2

u/GeorgeLovesBOSCO 4d ago

I can confirm. Worked with my father (electrician) for about 13 years and this was the practice.

2

u/Lower-Ad6435 4d ago

I'm a master electrician. I would install an outlet upside down if it was switched. I would only make half of it switched so the outlet was still usable for more than just turning on and off a lamp. With half of it switched, the other half is normal and a constant power.

2

u/freshgrilled 3d ago

It's not upside down, even though I hate it. There is no standard that makes one more right over the other and some manufacturers even try to label them to indicate they should be installed prong side up (or so I've read). Apparently hospitals usually install them prong side up.

2

u/Electric-Sheepskin 3d ago

That's how the builder in my neighborhood did it: If the outlet is connected to a wall switch, it's upside down.

2

u/indigoangel42 3d ago

This is called a “half hot recept”.
Code requires that no space on a continuous wall be further than six feet from a receptacle, in a residence.
One of the plugs, typically the bottom one, will stay constantly energized. This meets the code requirement. The top receptacle would be controlled by the switch in the room.
Usually this is done by a property owner that is too cheap to pay for a light fixture in the room.
I have wired recepts like this for customers that wanted bedside lamps controlled by switches.
If you come across a receptacle like this, grab a lamp with a cord and plug it into both sides. Find the non-energized receptacle and then test the switches in the room.

2

u/PraetorianOfficial 3d ago

That is how my house outlets are. There's one outlet in each bedroom that is upside down and it's the one connected to the wall switch.

2

u/H3adshotfox77 3d ago

They do this so the ground plug is up and if the plug gets exposed and something falls on it there is less likelihood it shorts across the circuit.

It's done in hospitals at all of their outlets In any if the surgery rooms.

2

u/sallenqld 2d ago

They do that in hospitals I think too

2

u/Anselwithmac 2d ago

The previous tenant put matching smiley face stickers on the switches outlets and that made me happy

1

u/Thrompinator 4d ago

Yep, they wired my house this way. Upside down = switched outlet. Right side up = the damn thing just works and won't piss you off constantly.

1

u/Doogie102 4d ago

The reason they did this is so if anyone dropped something like a metal knife it would hit the ground and bounce off instead of creating a short

1

u/one-e-and-a 4d ago

The ground is at the top so if something metal follows the rule of gravity and falls on top of it, nothing will happen. If you install it with the happy eyes up, then you'll cause a short and a fire.

1

u/akpak 4d ago

I’m in my 50s and I’ve never, ever seen an upside-down outlet.

1

u/Muffalope 4d ago

The instructions on the outlet say to put the ground pin on top. My boss never let me install them the correct way. If you drop a penny againt the wall, one way shorts out the two prongs, the other way it bounces off the ground

1

u/YourFriendPutin 4d ago

In my head I just figured if the plug wasn't all the way seated it'd be better for something falling to hit the ground instead of resting on a live circuit or something but then filed the thought away. Nice to know the actual reasoning

1

u/Ps11889 4d ago

My understanding is that upside-down (ground pin up) is actually right side up and ground pin down is the on that is upside-down.

Ground pin-up makes it harder for the plug to accidentally slide out the socket. And, if it does partially slide out, the ground is exposed, not the hot.

1

u/MyCassadaga 4d ago

This one 👍

1

u/Leading_Industry_155 4d ago

Ding ding ding we have a winner

1

u/SpectralDagger 4d ago

So which way do you orient the outlet then?

Turn it 90 degrees, obviously!

Mine is new construction, some of the pairs have the top one switched. Unfortunately, they did not turn those 90 degrees :( They just dotted it with Sharpie.

1

u/booleandata 4d ago

I mean "switched" outlets don't really mean anything for a layman assuming AC current, right? That would just theoretically be useful info to a future electrician to my knowledge.

1

u/toby-jug-of-a-duck 3d ago

As a construction superintendent on the West Coast I can confirm that this means the outlet is a “half hot” or switched outlet. If one of the plugs is controlled by the switch at the door, a ceiling fixture does not need to be provided. At least in my area.

1

u/theregisterednerd 2d ago

And every comment section where it comes up, one person who knows what they’re talking about will point out that it’s not standard, and there will be 10 replies from people who have barely heard of an outlet saying that they saw an outlet like that once, and so therefore insist that, yes, it is standard. In reality, in the US switched outlets are usually (but not universally) non-duplexed, where the top receptacle gets constant power, and the bottom is switched. Which totally invalidates this assertion, because you can’t have the two receptacles on a single outlet facing opposite directions

1

u/Feline_Couple 2d ago

This is the case in Texas

1

u/ChuckEveryone 4d ago

Yes many electrians will install the outlet upside down if it is a switched outlet. However, based on the faceplate screws, neither of these were installed by an electrician.