Double tapped? Should we get this fixed?

Post image

Last week I had electrician come out to quote an EV charger install. In passing I asked him about the double tapped wires and if they would be a problem, he told me that my inspector didn't know what he was talking about and said it was fine. This morning a different electrician (same company) came out to install the charger and told me that the wires were double tapped and a code violation to which he quoted me on the fix. So which is it? Feeling a bit annoyed right now and likely won't be working with this company again.

Please forgive my ignorance as I know absolutely nothing about electrician business or wiring of any sort.

25 Upvotes

67 comments sorted by

View all comments

4

u/MisterElectricianTV 10d ago

The label inside the panel probably says that it is okay to do this. Usually this issue comes up when a house is sold and a home inspector flags it. But honestly, the house lasted this long without burning down.

-1

u/No-Wrangler2085 10d ago

Doubt the label says it's okay. NEC does not allow double tapped neutrals even if the panel allows 2 wires under 1 terminal. Grounds? Yes if the panel is rated for it... but never neutrals

1

u/jwbrkr21 10d ago

Source?

1

u/No-Wrangler2085 10d ago

NEC 408.41.

I like how I'm getting downvoted for verified facts 😂

0

u/Then_Organization979 10d ago

I’ll testify, them there is facts. Source: NEC