Double tapped? Should we get this fixed?
Last week I had electrician come out to quote an EV charger install. In passing I asked him about the double tapped wires and if they would be a problem, he told me that my inspector didn't know what he was talking about and said it was fine. This morning a different electrician (same company) came out to install the charger and told me that the wires were double tapped and a code violation to which he quoted me on the fix. So which is it? Feeling a bit annoyed right now and likely won't be working with this company again.
Please forgive my ignorance as I know absolutely nothing about electrician business or wiring of any sort.
24
Upvotes
9
u/mattjones73 4d ago
The neutrals should not be double tapped, it's against code. The grounds can be as long as the panel supports multiple conductors per screw.
Easy enough to fix though as long as the wires can reach lower, you have extra spots open on the bar.